A036 alarm in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
435 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A036 alarm in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : No armature current can flow (active in operating states of – –, I, II)

This monitoring function responds if the armature firing angle is at the rectifier stability limit for more than 500 ms and the armature current is less than 1% of the converter rated armature DC current.