How can resolve problem A037 alarm in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : I2t motor monitor has responded (active in operating states of – –, I, II)

The alarm is activated when the calculated I2t value of the motor reaches the value which corresponds to the final temperature at 100% of permissible continuous motor current (= P113*P100).