Forum

Share:
Notifications
Clear all

F038 fault in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
565 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F038 fault in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Overspeed (active in operating states of – –, I, II)

This fault message is activated if the actual speed value (selected in P595) exceeds the positive (P380) or negative (P381) threshold by 0.5%.

Possible fault causes
Lower current limit has been input
Current-controlled operation
P512, P513 are set too low
Tachometer cable contact fault in operation close to maximum speed

Reply
Share: