How can resolve problem F038 fault in siemens 6RA70 DC Drive ?


1 Reply
Posts: 20042
Admin
Topic starter
(@click2electro)
Member
Joined: 5 years ago

Cause : Overspeed (active in operating states of – –, I, II)

This fault message is activated if the actual speed value (selected in P595) exceeds the positive (P380) or negative (P381) threshold by 0.5%.

Possible fault causes
Lower current limit has been input
Current-controlled operation
P512, P513 are set too low
Tachometer cable contact fault in operation close to maximum speed