F068 fault in siemens 6RA70 DC Drive

2 Posts
1 Users
0 Reactions
1,262 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F068 fault in siemens 6RA70 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Analog measuring channel faulty (main setpoint, main actual value or analog select input)
(active in all operating states) Hardware monitoring of measuring circuits

Possible fault causes
A7001 module defective
Measuring circuit saturated (input voltage at terminals 4 and 5 or 6 and 7 higher than approx. 11.3V)

Fault value:

1 Measuring channel for main setpoint / analog select input 1 faulty (terminals 4 and 5)
2 Measuring channel for main actual value faulty (terminals 103 and 104)
3 Measuring channel for analog select input 1 faulty (terminals 6 and 7)