How can resolve problem A01069 alarm in siemens 6RA80 DC Drive ?
1 Reply
Jun 13, 2022 5:17 pm
Cause : Parameter backup and device incompatible. The parameter backup on the memory card and the device type do not match (e.g. a memory card with the parameter backup of a SINAMICS S120 is inserted in SINAMICS G150).
The module boots with the factory settings.
Remedy:
- insert a memory card with compatible parameter backup and carry out a POWER ON.
- insert a memory card without parameter backup and carry out a POWER ON.
- backup parameters (p0977=1).