Siemens 6RA80 DC Drive
2
Posts
1
Users
0
Reactions
181
Views
Jun 13, 2022 5:18 pm
How can resolve problem A01069 alarm in siemens 6RA80 DC Drive ?
1 Reply
Jun 13, 2022 5:19 pm
Cause : Parameter backup and device incompatible. The parameter backup on the memory card and the device type do not match (e.g. a memory card with the parameter backup of a SINAMICS S110 is inserted in SINAMICS DCM).
The module boots with the factory settings.
Remedy:
- insert a memory card with compatible parameter backup and carry out a POWER ON.
- insert a memory card without parameter backup and carry out a POWER ON.
- remove the memory card and carry out POWER ON.
- backup parameters (p0971=1).