How can resolve problem A01099 alarm in siemens 6RA80 DC Drive ?
1 Reply
Jun 13, 2022 5:20 pm
Cause : Tolerance window of time synchronization exited. The time master exited the selected tolerance window for time synchronization. See also: p3109 (RTC real time synchronization, tolerance window)
Remedy: Select the re-synchronization interval so that the synchronization deviation between the time master and drive system lies within the tolerance window.
See also: r3108 (RTC last synchronization deviation)