Cause : De-activated component again present comes when a component of the target topology for an active drive object is inserted and the associated parameter of the component is set to "de-activate" (p0125, p0145, p0155, p0165).
Note: This is the only message that is displayed for a de-activated component.
Remedy:
The alarm automatically disappears again with the following actions:
- activate the components involved (p0125 = 1, p0145 = 1, p0155 = 1, p0165 = 1).
- again withdraw the components involved.
See also: p0125 (Activate/de-activate power unit components), p0145 (Activate/de-activate encoder interface)
1 Reply
Admin
Topic starter
(@click2electro)
Member
Cause : De-activated component again present. If a component of the target topology for an active drive object is inserted and the associated parameter of the component is set to "de-activate" (p0125, p0145, p0155, p0165).