Forum

Share:
Notifications
Clear all

A01318 alarm in siemens 6RA80 DC Drive

2 Posts
1 Users
0 Reactions
275 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : De-activated interconnections present comes when an inactive/non-operational drive object is active againready for operation.

This alarm is used in the following cases:

- If an inactive/non-operational drive object is active again/ready for operation
- If there are items in the list of BI/CI parameters (r9498[0...29], r9499[0...29])
- If the BICO interconnections saved in the list of BI/CI parameters (r9498[0...29], r9499[0...29]) have actually been changed

Remedy:

Reset alarm:
- Set p9496 to 1 or 2
- de-activate the drive object again.

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : BICO: De-activated interconnections present.

This alarm is used in the following cases:
- If an inactive/non-operational drive object is active again/ready for operation
- If there are items in the list of BI/CI parameters (r9498[0...29], r9499[0...29])
- If the BICO interconnections saved in the list of BI/CI parameters (r9498[0...29], r9499[0...29]) have actually been changed

Remedy:

Reset alarm:
- Set p9496 to 1 or 2
or
- de-activate the drive object again.

Reply
Share: