Siemens 6RA80 DC Drive
1
Posts
1
Users
0
Reactions
75
Views
Sep 23, 2024 9:17 am
F30081 fault in siemens 6RA80 DC Drive indicate that the switching operations too frequent. This means the power unit has executed too many switching operations for current limitation.
- Check the motor data - if required, carry out commissioning.
- U/f operation: Increase up ramp.
- U/f operation: Check assignment of rated currents of motor and power unit.
- Check the power cable connections.
- Check the power cables for short-circuit or ground fault.