F30801 fault in siemens 6RA80 DC Drive indicate Sign-of-life missing. This means a DRIVE-CLiQ communication error has occurred from the Control Unit to the power unit concerned. The computing time load might be too high.
- Check the electrical cabinet design and cable routing for EMC compliance
- Remove DRIVE-CLiQ components that are not required.
- De-select functions that are not required.
- If required, increase the sampling times (p0112, p0115).
- Replace the component involved.