Forum

Share:
Notifications
Clear all

A2026 INPUT PHASE LOSS alarm in ABB ACS150

3 Posts
1 Users
0 Reactions
2,124 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A2026 INPUT PHASE LOSS alarm in ABB ACS150 ?

2 Replies
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Intermediate circuit DC voltage is oscillating due to missing input power line phase or blown fuse.

Alarm is generated when DC voltage ripple exceeds 14% of nominal DC voltage.

Programmable fault function

parameter - 3016 SUPPLY PHASE

1.Check input power line fuses.
2. Check for input power supply imbalance.
3. Check fault function parameter setting.

Reply
Posts: 18330
Share: