How can resolve problem A5013 alarm in ABB ACS150 ?
Cause : Panel control is disabled because start inhibit is active.
1. Start from the panel is not possible.
2. Reset the emergency stop command or remove the 3-wire stop command before starting from the panel.
Cause : Button is disabled, because start is inhibited.
set parameter
2108 - 0 (Disables the Start inhibit function.)
1601 - 0 (Disable run enable)
2109 - 0
Sets the Start inhibit function on or off.
If the drive is not actively started and running, the Start inhibit function ignores a pending start command in any of the following situations and a new start command is required.
• A fault is reset.
• Run Enable (parameter 1601) activates while start command is active.
• Mode changes from local to remote.
• Control switches from EXT1 to EXT2.
• Control switches from EXT2 to EXT1