Forum

Share:
Notifications
Clear all

F1013 PAR PFC IO 2 Fault in ABB ACS310 Drive

2 Posts
1 Users
0 Reactions
779 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F1013 PAR PFC IO 2 Fault in ABB ACS310 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : I/O configuration for PFC not complete.

Check parameter settings. Following must apply:

The actual number of PFC motors (parameter 8127 MOTORS) matches the PFC motors in parameter group 14 RELAY OUTPUTS

and parameter 8118 AUTOCHNG INTERV.

Reply
Share: