How can resolve problem F1013 PAR PFC IO 2 Fault in ABB ACS310 Drive ?
1 Reply
Dec 18, 2021 11:24 am
Cause : I/O configuration for PFC not complete.
Check parameter settings. Following must apply:
• The actual number of PFC motors (parameter 8127 MOTORS) matches the PFC motors in parameter group 14 RELAY OUTPUTS
and parameter 8118 AUTOCHNG INTERV.