A5013 alarm in ABB ACS355

3 Posts
1 Users
0 Reactions
2,578 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A5013 alarm in ABB ACS355 ?

2 Replies
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Panel control is disabled because start inhibit is active.

Start from panel is not possible.

Reset emergency stop command or remove 3-wire stop command before starting from panel.

See section 3-wire macro and

parameters 1001 EXT1 COMMANDS,

1002 EXT2 COMMANDS and

2109 EMERG STOP SEL.

Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Button is disabled, because start is inhibited.

set parameter

2108 - 0 (Disables the Start inhibit function.)

1601 - 0 (Disable run enable)

2109 - 0

Sets the Start inhibit function on or off.

If the drive is not actively started and running, the Start inhibit function ignores a pending start command in any of the following situations and a new start command is required.

A fault is reset.
Run Enable (parameter 1601) activates while start command is active.
Mode changes from local to remote.
Control switches from EXT1 to EXT2.
Control switches from EXT2 to EXT1

Reply