F1009 fault in ABB ACS355 drive

1 Posts
1 Users
0 Reactions
239 Views
Posts: 17277
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : PAR PCU 1 comes when incorrect motor nominal speed/frequency setting. This means the drive has detected a conflict within the settings that govern how the drive controls the power delivered to the motor.

  1. Check parameter settings. Following must apply for induction motor:
    • 1 < (60 · 9907 MOTOR NOM FREQ / 9908 MOTOR NOM SPEED) < 16
    • 0.8 < 9908 MOTOR NOM SPEED / (60 · 9907 MOTOR NOM FREQ / 9913 MOTOR POLE PAIRS) < 0.992
  2. Following must apply for permanent magnet synchronous motor:
    • 9908 MOTOR NOM SPEED / (60 · 9907 MOTOR NOM FREQ / 9913 MOTOR POLE PAIRS) = 1.0