FF61 ID run Fault in ABB ACS380 Drive

4 Posts
2 Users
0 Likes
4,222 Views
Posts: 14733
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem FF61 ID run Fault in ABB ACS380 Drive ?

3 Replies
Posts: 14733
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Motor ID run was not completed successfully.

1. Check the nominal motor values in parameter group 99 Motor data.

2. Check that no external control system is connected to the drive.

3. Cycle the power to the drive (and its control unit, if powered separately).

4. Check that no operation limits prevent the completion of the ID run. Restore parameters to default settings and try again.

5. Check that the motor shaft is not locked.

6. After this facing any problem then contact us.

Reply
1 Reply
(@khemjilal-mohanta)
Joined: 1 year ago

New Member
Posts: 1

@click2electro 

FF61 code in display when I m puss start bottom

Reply
Posts: 14733
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

First take drive in local mode then

set parameter 99.13 - 3

then press start button on drive display then Drive ID run function performed wait 1 min and check any fault coming or not. Then change control mode local to remote and start drive by push button.

Reply