A2005 IO COMM Alarm in ABB ACS550 Drive

2 Posts
1 Users
0 Reactions
392 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A2005 IO COMM Alarm in ABB ACS550 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Fieldbus communication has timed out. Check for and correct:
Fault setup (3018 COMM FAULT FUNC and 3019 COMM FAULT TIME).
Communication settings

(Group 51: EXT COMM MODULE or Group 53: EFB PROTOCOL as appropriate).
Poor connections and/or noise on line

Reply