3210 DC link overvoltage Fault in ABB ACS560 Drive

2 Posts
1 Users
0 Likes
1,409 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem 3210 DC link overvoltage Fault in ABB ACS560 Drive ?

1 Reply
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Excessive intermediate circuit DC voltage.

1. Check that overvoltage control is on (parameter 30.30 Overvoltage control).

2. Check that the supply voltage matches the nominal input voltage of the drive.

3. Check the supply line for static or transient overvoltage.

4. Check brake chopper and resistor (if present).

5. Check deceleration time.Use coast-to-stop function (if applicable).

6. Retrofit drive with brake chopper and brake resistor.