7510 COMM MODULE Fault in ABB ACS800 Drive

2 Posts
1 Users
0 Reactions
4,577 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem 7510 COMM MODULE Fault in ABB ACS800 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Cyclical communication between drive and master is lost.

(programmable Fault Function 30.18, 30.19)

Check status of fieldbus communication. See
chapter Fieldbus control, or appropriate
fieldbus adapter manual.
Check parameter settings:
- group 51 COMM MODULE DATA(for fieldbus
adapter), or
- group 52 STANDARD MODBUS (for
Standard Modbus Link).
Check Fault Function parameters.
Check cable connections.
Check if master can communicate