How can resolve problem 7510 COMM MODULE Fault in ABB ACS800 Drive ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
Cause : Cyclical communication between drive and master is lost.
(programmable Fault Function 30.18, 30.19)
Check status of fieldbus communication. See
chapter Fieldbus control, or appropriate
fieldbus adapter manual.
Check parameter settings:
- group 51 COMM MODULE DATA(for fieldbus
adapter), or
- group 52 STANDARD MODBUS (for
Standard Modbus Link).
Check Fault Function parameters.
Check cable connections.