F0039 ENCODER 1 Fault in ABB ACS850 Drive
How can resolve problem F0039 ENCODER 1 Fault in ABB ACS850 Drive ?
Cause : Encoder 1 feedback fault.
If fault appears during first start-up before
encoder feedback is used:
- Check cable between encoder and
encoder interface module (FEN-xx) and
order of connector signal wires at both
ends of cable.
If fault appears after encoder feedback
has already been used or during drive
run:
- Check that encoder connection wiring
or encoder is not damaged.
- Check that encoder interface module
(FEN-xx) connection or module is not
damaged.
- Check earthings (when disturbances
are detected in communication between
encoder interface module and encoder).
For more information on encoders, see
parameter groups 90 Enc module sel, 92
Resolver conf and 93 Pulse enc conf.