F0032 OVERSPEED Fault in ABB ACSM1 Drive

2 Posts
1 Users
0 Reactions
783 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F0032 OVER SPEED Fault in ABB ACSM1 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Motor is turning faster than highest allowed speed due to incorrectly set minimum/ maximum speed, insufficient braking torque or changes in load when using torque reference.

Check minimum/maximum speed settings,
parameters 20.01 MAXIMUM SPEED and
20.02 MINIMUM SPEED.
Check adequacy of motor braking torque.
Check applicability of torque control.
Check need for braking chopper and resistor(s).