Cause : Motor 1 field exciter communication loss comes when communication error occurs, it can disrupt the drive's operation and prevent it from functioning correctly.
F516 M1FexCom fault in ABB DCS800 drive indicate Motor 1 field exciter communication loss. This means a communication error between the drive and the M1FexCom module.
- Check flat cable connections between SDCS-CON-4 and SDCS-PIN-4.
- Check auxiliary voltage for integrated and external field exciter.
- Check DCSLink cable connections.
- Check DCSLink termination set dip switch S1100:1 = ON (DCF803-0016, DCF803-0035 and FEX- 425-Int).