How can resolve problem 4981 Motor temperature 1 measured/estimated Fault In ABB DCS880 ?
Measured/Estimated motor temperature 1 has exceeded the fault level. See also A491. Wait until the motor/motor model is cooled down under the
warning level. The fan contactor stays on as long as the fault is pending. It is not possible to reset the fault as long as the motor remains too hot.
Check:
− The value of 35.02 Measured temperature 1.
− The real motor temperature. Let motor cool down and restart.
− The value of 35.12 Temperature 1 fault level.
− The cooling of the motor or other temperature measured equipment.
− The ambient conditions (e.g. ambient temperature).
− The airflow and fan operation.
− The motor fan supply voltage.
− The motor fan direction of rotation.
− The motor fan components.
− The motor cooling air inlet (e.g. filters).
− The motor cooling air outlet.
− The motor load and drive ratings.
− Inadmissible load cycle.
− The wiring of the temperature sensor.
− The resistance of the temperature sensor by measuring it.
Hint:
− The measured/estimated motor temperature is blocked, if
35.11 Temperature 1 source = Disable