How can resolve problem 73B0 Emergency ramp stop Fault In ABB DCS880 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Emergency stop did not finish within the expected time.
Check:

The settings of 31.31 Emergency ramp supervision and
31.32 Emergency ramp supervision delay.

The settings of parameters 23.11 ... 23.19 for Off3 stop
mode 1 (21.03 Emergency stop mode = Ramp stop).

The setting of 23.23 Emergency stop time for Off3 stop
mode 2 (21.03 Emergency stop mode = Emergency ramp
stop).

The current and torque limits in group 30 Control limits.