How can resolve problem A497 Motor temperature slot1 measured warning In ABB DCS880 ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
The thermistor protection module (FEN-xx or FPTC- xx) installed in slot1 indicates over temperature.
Depending on the used module, a PTC and/or KTY temperature sensor can be attached. See also 4991 ... 4993.
The cooling of the motor or other temperature measured equipment.
The motor load and drive ratings.
The wiring of the temperature sensor.
The resistance of the temperature sensor by measuring it.Check