A4A0 Control board temperature measured warning In ABB DCS880

2 Posts
1 Users
0 Reactions
409 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A4A0 Control board temperature measured warning In ABB DCS880 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Excessive control board temperature. Check the auxiliary code (format XXXX ZZZZ). ZZZZ indicates the problem.

Actions see below.

None

Temperature above warning limit of xx °C or xx °F.
Check:

The value of 05.10 Control board temperature.

The ambient conditions.

The airflow and fan operation.

The heatsink fins for dust pick-up.

0001

Thermistor broken.