Forum
Share:
Notifications
Clear all
A581 Drive fan acknowledge warning In ABB DCS880
1 Users
0 Reactions
Admin
Topic starter
(@click2electro)
Member
How can resolve problem A581 Drive fan acknowledge warning In ABB DCS880 ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
Programmable, see 31.41 Main fan fault function
Drive cooling fan feedback at the DI is missing. See also 5080.
Check:
The settings of 20.38 Drive fan acknowledge source and 20.40 Drive/Motor fan delay time.
The drive fan operation and connection.
The drive fan contactor.
The drive fan circuit.
The drive fan klixon.
The drive fan components.
The drive fan supply voltage.
The drive fan direction of rotation.
The drive door open.
The drive cooling air inlet (e.g. filter).
The drive cooling air outlet.
H7 an H8 pressure switch (setting should be 2 mbar).
The used digital inputs and outputs (groups 10 and 11).