A5A3 Safe off main contactor XSTOMC warning In ABB DCS880

2 Posts
1 Users
0 Reactions
194 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A5A3 Safe off main contactor XSTOMC warning In ABB DCS880 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Programmable, see 31.90 XSTOMC Indication

STO monitor DC current not zero. See safety supplement for functional safety converter DCS880 (3ADW000452). See also B5A3 and 5093.