F503 Armature overvoltage Fault In ABB DCS880

2 Posts
1 Users
0 Reactions
1,128 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F503 Armature overvoltage Fault In ABB DCS880 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Too high voltage on the armature/DC side.

Check:

If the setting of 31.50 Overvoltage level is suitable for the
system.

The settings of the field current controller, EMF controller,
flux linearization in group 28 EMF and field current control.
E.g. field weakening is not activated.

For too high field current (e.g. problems with field
weakening).

If the motor was accelerated by the load.

For overspeed.

For proper speed scaling. See 46.02 M1 speed scaling
actual.

For proper armature voltage feedback.

The cutting of the voltage coding resistors on the SDCS-
PIN-H51.