Forum

Share:
Notifications
Clear all

F524 Main contactor acknowledge Fault In ABB DCS880

2 Posts
1 Users
0 Likes
409 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem F524 Main contactor acknowledge Fault In ABB DCS880 ?

1 Reply
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Main contactor acknowledge at the DI is missing.
Check:

− The settings of 20.33 Main contactor control mode and 20.34 Main contactor acknowledge source.

− The switch on/off sequence.

− The auxiliary contactor/relay switching the main contactor after an On/Off command.

− The safety relays if existing.

− The used digital inputs and outputs (groups 10 and 1
1)

Reply
Share: