How can resolve problem F541 M1 field exciter low current Fault In ABB DCS880 ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
Motor 1 field exciter low (under-) current.
Check:
The settings of 31.57 Minimum field current trip delay and
31.58 M1 field current low level.
The settings of the EMF controller, flux linearization and field
current controller in group 28 EMF and field current control.
The motor nameplate for minimum current at maximum field
weakening ≡ maximum speed.
The field circuit fuses.
The field auxiliary supply voltage.
The field contactor is not closed.
If the field current oscillates.
If the motor is not compensated and has a high armature
reaction.
For fault messages at the field exciter itself (flashing LEDs),
04.26 M1 field exciter fault word and 04.36 M1 field exciter
warning word.