What is ABB fault 1 over current ?

2 Posts
1 Users
0 Reactions
1,124 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

If OVERCURRENT Output current is excessive then this fault coming. Check for and correct: Excessive motor load, check motor parameter and motor connection.

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Output current is excessive due to load, wrong parameter or sensing problem in control card of drive and some time faulty motor. These are the step for fault correction :

1. Check motor load, due to motor overload drive generate fault.

2. Check motor data in drive parameter.

3. Check output current and compare with clamp-meter.

4. Check drive IGBT using multi-meter.

5. Check current sensing circuit in drive.

 