Warnings /Alarms 13 Overcurrent in VLT Micro Drive FC51

1 Posts
1 Users
0 Reactions
820 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Warnings /Alarms 13 in VLT Micro Drive FC51 - means comes when drive peak current limit is exceeded. Remove power and check if the motor shaft can be turned.

1. The inverter peak current limit (approximately 200% of the rated current) is exceeded. The warning lasts approximately 1.5 s, then the drive trips and issues an alarm.

Shock loading or quick acceleration with high-inertia loads can cause this fault. If the acceleration during ramp-up is quick, the fault can also appear after kinetic back-up. If extended mechanical brake control is selected, a trip can be reset externally.

2. The inverter peak current limit (approximately 200% of the rated current) is exceeded. The warning lasts approximately 1.5 s, then the drive trips and issues an alarm. Shock loading or quick acceleration with high-inertia loads can cause this fault.