Danfoss Vacon 100X, 100 Flow & 100 Industrial Drive
1
Posts
1
Users
0
Reactions
124
Views
Mar 07, 2024 10:10 am
Cause : Temperature fault 2 comes when 1 or more of the temperature input signals (set in P3.9.6.5) is higher than the fault limit (P3.9.6.6) or 1 or more of the temperature input signals (set in P3.9.6.5) is higher than the fault limit (P3.9.6.7).
- Find the cause of the temperature rise.
- Do a check of the temperature sensor and connections.
- If no sensor is connected, make sure that the temperature input is hardwired.