Danfoss VLT 2800 Drive
1
Posts
1
Users
0
Reactions
104
Views
Oct 04, 2024 7:36 am
Err2 fault in danfoss VLT2800 drive indicate Live zero error. This means the signal on one of the analog inputs is less than 50% of the minimum value programmed for that input. Broken wiring or faulty device sending the signal can cause this condition.
- Check connections on all the analog input terminals.
- Control card terminals 53 and 54 for signals, terminal 55 common.
- MCB 101 terminals 11 and 12 for signals, terminal 10 common.
- MCB 109 terminals 1, 3, 5 for signals, terminals 2, 4, 6 common).
- Check that the frequency converter programming and switch settings match the analog signal type.
- Perform an input terminal signal test.