Warning /Alarm 59 in danfoss VLT FC360 drive : Current Limit - comes when the current is higher than the value in parameter 4-18 Current Limit.

1. Ensure that the motor data in parameters 1-20 to 1-25 is set correctly.
2. Increase the current limit if necessary. Ensure that the system can operate safely at a higher limit