Forum

Share:
Notifications
Clear all

Warning /Alarm 59 in danfoss VLT FC360 drive

1 Posts
1 Users
0 Reactions
2,990 Views
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Warning /Alarm 59 in danfoss VLT FC360 drive : Current Limit - comes when the current is higher than the value in parameter 4-18 Current Limit.

1. Ensure that the motor data in parameters 1-20 to 1-25 is set correctly.
2. Increase the current limit if necessary. Ensure that the system can operate safely at a higher limit

Share: