Forum

Share:
Notifications
Clear all

WARNING/ALARM 22 in danfoss FCD302 drive

1 Posts
1 Users
0 Reactions
143 Views
Posts: 18023
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Hoist Mechanical Brake - This alarm occurs when the torque reference was not reached before timeout (parameter 2-27 Torque Ramp Up Time).

  1. Check if mechanical brake is broken or opened before start.
  2. Check if parameter 2-27 Torque Ramp Up Time is too short.
Share: