How can resolve problem ocd fault in delta C200 series drive ?
1 Reply
Apr 25, 2022 11:35 am
Cause : Over-current during deceleration
(Output current exceeds triple rated current during deceleration.)
Corrective Actions:
1. Short-circuit at motor output: Check for possible poor
insulation at the output line.
2. Deceleration Time too short: Increase the Deceleration Time.
3. AC motor drive output power is too small: Replace the AC
motor drive with the next higher power model.