Forum

Share:
Notifications
Clear all

ocd fault in delta C200 series drive

2 Posts
1 Users
0 Reactions
351 Views
Posts: 18126
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem ocd fault in delta C200 series drive ?

Topic Tags
1 Reply
Posts: 18126
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Over-current during deceleration
(Output current exceeds triple rated current during deceleration.)
Corrective Actions:
1. Short-circuit at motor output: Check for possible poor
insulation at the output line.
2. Deceleration Time too short: Increase the Deceleration Time.
3. AC motor drive output power is too small: Replace the AC
motor drive with the next higher power model.

Reply
Share: