How can resolve problem EoL2 fault in delta C2000 series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Electronic thermal relay 2 protection (EoL2)

Electronic thermal relay 2 protection. The drive coasts to stop once it activates.

The load is too large - Reduce the load.

Action condition - Start counting when output current > 105% of motor 2 rated current.

Action time - Pr.06-28 (If the output current is larger than 105% of motor 2 rated current again
within 60 sec., the counting time reduces and is less than Pr.06-28)

Decrease low-speed operation time.
Replace the drive with a dedicated to VFD model.

Increase the motor capacity.
Check drive rectifier & IGBT using multimeter.
Check wiring.
Check drive hardware using multimeter.