Forum

Share:
Notifications
Clear all

oH3 fault in delta C2000 series drive

2 Posts
1 Users
0 Reactions
326 Views
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem oH3 fault in delta C2000 series drive ?

1 Reply
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Motor overheating (oH3)

The load is too large -

Reduce the load.
Increase the motor capacity.

Ambient temperature is too high -

Change the installed place if there are heating devices in the surroundings.
Install/ add cooling fan or air conditioner to lower the ambient temperature

Operate at low-speed too long -

Decrease low-speed operation time.
Replace the motor with a dedicated to VFD model.

Increase the motor capacity.

Fault treatment parameter

Pr.06-29
0: Warn and keep operation

1: Fault and ramp to stop

2: Fault and coast to stop

3: No warning

Reply
Share: