Forum

Share:
Notifications
Clear all

ot1 fault in delta C2000 series drive

2 Posts
1 Users
0 Reactions
1,081 Views
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem ot1 fault in delta C2000 series drive ?

1 Reply
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Over torque 1 (ot1)

When output current exceeds the over-torque detection level (Pr.06-07) and exceeds over-torque detection time (Pr.06-08), and when Pr.06-06 or Pr.06-09 is set to 2 or 4, the ot1 error displays.

Incorrect parameter setting - Reset Pr.06-07 and Pr.06-08

The load is too large -

Reduce the load.
Replace the motor with a larger capacity model
.

Fault treatment parameter

Pr.06-06
0: No function

1: Continue operation after Over-torque detection during constant speed
operation

2: Stop after Over-torque detection during constant speed operation

3: Continue operation after Over-torque detection during RUN

4: Stop after Over-torque detection during RUN

 

Reply
Share: