ot1 warning in delta C2000 series drive

2 Posts
1 Users
0 Reactions
342 Views
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve ot1 warning in delta C2000 series drive ?

1 Reply
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Over-torque 1 (ot1)

Over-torque 1 warning

Incorrect parameter setting - Configure the settings for Pr.06-07 and Pr.06-08 again.

The load is too large -

Decrease the loading.
Replace with a motor with larger capacity.

Warning setting parameter

Pr.06-06 = 1 or 3
0: No function

1: Continue operation after over-torque detection during constant speed
operation

2: Stop after over-torque detection during constant speed operation

3: Continue operation after over-torque detection during RUN

4: Stop after over-torque detection during RUN

Reply