uC Under current fault in delta C2000 series drive

2 Posts
1 Users
0 Reactions
333 Views
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem uC Under current fault in delta C2000 series drive ?

Topic Tags
1 Reply
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Under current (uC)

Low current detection.

Improper setting of low-current protection - Reset Pr.06-71, Pr.06-72 and Pr.06-73 to proper settings.

The load is too low -

Check the load status.
Check if the motor capacity matches the load
.

Fault treatment parameter

Pr.06-73
0: No function

1: Fault and coast to stop

2: Fault and ramp to stop by second deceleration time

3: Warn and operation continue

When Pr.06-73 = 3, uC is a “Warning”. The warning is automatically cleared when the output current > (Pr.06-71+0.1 A).

When Pr.06-73 = 1 or 2, uC is a “Fault”. You must reset manually.

This fault also comes when you run drive without motor or rating of motor is small as compare to drive.