Forum

Share:
Notifications
Clear all

uC Under current warning in delta C2000 series drive

2 Posts
1 Users
0 Reactions
378 Views
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve uC Under current warning in delta C2000 series drive ?

Topic Tags
1 Reply
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Under current (uC) - Low current

“Warning” occurs when Pr.06-73 = 3. The “Warning” automatically clears when the output current is > (Pr.06-71 + 0.1A).

Warning setting parameter

Pr.06-73
0: No function

1: Fault and coast to stop

2: Fault and ramp to stop by second deceleration time

3: Warn and operation continue

This fault also comes when you run drive without motor or rating of motor is small as compare to drive.

 

Reply
Share: