ot2 warning in delta C2000 series drive

2 Posts
1 Users
0 Reactions
459 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve ot2 warning in delta C2000 series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Over-torque (ot2)

Incorrect parameter setting - Configure the settings for Pr.06-10 and Pr.06-11

The load is too large -

Decrease the loading.
Replace with a motor with larger capacity.

Warning setting parameter

Pr.06-09 = 1 or 3
0: No function

1: Continue operation after over-torque detection during constant speed
operation

2: Stop after over-torque detection during constant speed operation

3: Continue operation after over-torque detection during RUN

4: Stop after over-torque detection during RUN

Reply