How can resolve ot2 warning in delta C2000 series drive ?
1 Reply
May 14, 2022 4:50 am
Over-torque (ot2)
Incorrect parameter setting - Configure the settings for Pr.06-10 and Pr.06-11
The load is too large -
Decrease the loading.
Replace with a motor with larger capacity.
Warning setting parameter
Pr.06-09 = 1 or 3
0: No function
1: Continue operation after over-torque detection during constant speed
operation
2: Stop after over-torque detection during constant speed operation
3: Continue operation after over-torque detection during RUN
4: Stop after over-torque detection during RUN