How can resolve PID warning in delta C2000 series drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

PID feedback error (PID)

PID feedback loss (warning for analog feedback signal; works only when PID enables)

Action condition - When the analog input is lower than 4 mA (only detects analog input of 4–20 mA)

Warning setting parameter

Pr.08-09
0: Warn and keep operation

1: Fault and ramp to stop

2: Fault and coast to stop

3: Warn and operate at last frequency

“Warning” occurs when Pr.08-09 = 0 or 3. The “Warning” automatically
clears when the feedback signal is larger than 4 mA

Tighten the terminals again.
Replace with a new cable