Cause : GFF occurs before run comes when the ground short circuit detected when the output wiring detection is performed before the drive runs. This means the drive identifies a potential issue with grounding during its initial power-on checks.
The error code b4GFF in delta drive indicates a ground fault detected before the drive even starts (b4 stands for "before"). This means the drive identifies a potential issue with grounding during its initial power-on checks and prevents operation to ensure safety.
- Check if the motor’s internal wiring and the UVW wiring of the drive output terminal are correct.
- Check the motor cable and remove causes of the short circuits, or replace the cable before turning on the power.
- Check the motor insulation value with megger.
- Replace the motor if the insulation is poor.