STO fault in delta ME300 series drive

2 Posts
1 Users
0 Reactions
370 Views
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem STO fault in delta ME300 series drive ?

1 Reply
Posts: 14967
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : STO Safe Torque Off function activates.

Check the wiring of the S1 and S2 terminals.

Check if STO card is correctly installed.

Check that the input voltage maintains at least 11V.

When Pr.06-441 and after STO error is cleared, it automatically
resets.

When Pr.06-440 and after STO error is cleared, reset it manually.

Reset only after STO error is cleared.